    I have just a basic inverter that I got from an auto parts store. It came with short cables with clamps to connect to the battery. I want to hard wire it permanently, would it damage the inverter?, also would it be a fire hazard or something constantly connected, or drain the battery? This is what i have.

    http://www.oreillyauto.com/site/c/de...yword=inverter
    1994 K2500 Suburban 6.5 turbo diesel, 4l80e, 14bff, g80
    2000 Ford F250, v10, 4x4
    2010 Toyota Carolla S (My DD)
    2013 Ford Fusion (Her DD)
    1992 K2500 Suburban 454tbi, 4l80e, 14bff g80 (Sold but miss it)

  2. #2
    Join Date
    Nov 2010
    Location
    Middle of Nowhere, Outer Skin of Space Ship Earth, 1 A.U. from Sol, Outskirts of Milky Way.
    Posts
    2,087
    Sure, inverters are often hard-wired (the bigger ones pretty much always are).

    BUT...

    800w / 12v = 67 amps

    So you'll want to use some fairly hefty wire/fuse to feed that thing. I can pretty much guarantee that whatever size wire they gave you with the alligator clips is way too small to really handle 800w@12v. Cut a short section from a set of 4 gauge jumper cables and use a 70a breaker or fuse and you'll be good to go.

    You can get a set of sacrificial jumper cables pretty cheap:

    http://www.google.com/products/catal...d=0CJABEPMCMAA


    As for draining the battery - it depends. If it's switched off, it shouldn't be drawing from the battery at all. Just remember to switch it off, otherwise it will parasite drain the battery just sitting there.

    EDIT: And don't even think about running an 800w load unless the engine is running.
    Last edited by dwh; 04-19-2012 at 05:14 PM.
    ...
    ...
    Current: 76 E-250, bubble-top, self-contained|couple of old Yamaha enduros
    Previous wheelers: 41 Willys|78 FJ40|78 Bronco|84 Bronco|74 Ramcharger|78 Ramcharger|79 D150 PowerWagon|77 D100|79 D400 dually, converted to 4WD, utility bed, 10' Lance|75 Westy|69 Scout, RHD|bunch of others|bunch of bikes|couple of boats|couple of motorhomes|blah blah|so what|not my idea|just doin' what I'm told|wank wank|this space for rent|candy is dandy|but liquor is quicker

  3. #3
    Join Date
    Oct 2011
    Location
    Tucson, AZ
    Posts
    411
    Quote Originally Posted by dwh View Post
    Sure, inverters are often hard-wired (the bigger ones pretty much always are).

    BUT...

    800w / 12v = 67 amps

    So you'll want to use some fairly hefty wire/fuse to feed that thing. I can pretty much guarantee that whatever size wire they gave you with the alligator clips is way too small to really handle 800w@12v. Cut a short section from a set of 4 gauge jumper cables and use a 70a breaker or fuse and you'll be good to go.

    You can get a set of sacrificial jumper cables pretty cheap:

    http://www.google.com/products/catal...d=0CJABEPMCMAA


    As for draining the battery - it depends. If it's switched off, it shouldn't be drawing from the battery at all. Just remember to switch it off, otherwise it will parasite drain the battery just sitting there.

    EDIT: And don't even think about running an 800w load unless the engine is running.
    thanks for the input, yea the wires they provided are 8ga so i was just going to use longer 8ga to supply power to it, also would it have a integrated fuse or breaker since its meant to be a stand alone thing? either way doesnt hurt to add a fuse. I didnt even think about it being that high a load since it was a smaller inverter.
    1994 K2500 Suburban 6.5 turbo diesel, 4l80e, 14bff, g80
    2000 Ford F250, v10, 4x4
    2010 Toyota Carolla S (My DD)
    2013 Ford Fusion (Her DD)
    1992 K2500 Suburban 454tbi, 4l80e, 14bff g80 (Sold but miss it)

  4. #4
    Join Date
    Nov 2010
    Location
    Middle of Nowhere, Outer Skin of Space Ship Earth, 1 A.U. from Sol, Outskirts of Milky Way.
    Posts
    2,087
    It will likely have a fuse to protect its internal circuitry. That's a totally different thing than a fuse to protect the wire that feeds power to it.
    ...
    ...
    Current: 76 E-250, bubble-top, self-contained|couple of old Yamaha enduros
    Previous wheelers: 41 Willys|78 FJ40|78 Bronco|84 Bronco|74 Ramcharger|78 Ramcharger|79 D150 PowerWagon|77 D100|79 D400 dually, converted to 4WD, utility bed, 10' Lance|75 Westy|69 Scout, RHD|bunch of others|bunch of bikes|couple of boats|couple of motorhomes|blah blah|so what|not my idea|just doin' what I'm told|wank wank|this space for rent|candy is dandy|but liquor is quicker

  5. #5
    Join Date
    Dec 2007
    Location
    Santee, CA
    Posts
    1,241
    I think you're overestimating the need for larger wires... especially 4g.

    100 amps over distance:
    3ft-5ft 12 gauge wire
    7ft-10ft 10 gauge wire
    15ft-20ft 6 gauge wire
    25ft 4 gauge wire

    Anything you run should have a 70 amp breaker at each end, or a breaker at the battery end and a 70amp maxi fuse at the device end.
    Mitch
    → 1999 4Runner, 4WD, 4 tires and a spare, a lift, and some armor.

    My Build Thread

    My YouTube Channel

    Roaming the Land of the Free and the Home of the Brave - American Adventurist!

  6. #6
    Join Date
    Oct 2011
    Location
    Tucson, AZ
    Posts
    411
    Do you think 8ga wire then for a run of about 6ft would be heavy enough? Ill definitely add fuses, is there a reason you recommend a breaker at the battery end instead of 2 fuses? sorry if some of these questions seem dumb but the more i can learn about these small projects the easier and safer future larger electrical projects will be, electronics has always been my trouble area when building stuff.
    1994 K2500 Suburban 6.5 turbo diesel, 4l80e, 14bff, g80
    2000 Ford F250, v10, 4x4
    2010 Toyota Carolla S (My DD)
    2013 Ford Fusion (Her DD)
    1992 K2500 Suburban 454tbi, 4l80e, 14bff g80 (Sold but miss it)

  7. #7
    Join Date
    Mar 2012
    Location
    California
    Posts
    72
    Quote Originally Posted by dwh View Post
    Sure, inverters are often hard-wired (the bigger ones pretty much always are).

    BUT...

    800w / 12v = [B]67 amps
    In straight math yes but batteries are do not always put out 12V. Also inverters are not 100% efficient so input could be higher than what appears to be needed to make the rated output. Always make your plans on the safe side. Use 10 volts whenever sizing wire for your inverter. Thus your 800W inverter could draw as much as 80 amps. So I'd suggest sizing you wire according to that.

    According to the table I use (near the bottom) http://www.rbeelectronics.com/wtable.htm

    I'd be safe and run 6 gauge, which should also be easy to source by getting an amp install kit from your local car audio dealer
    Last edited by lqdchkn; 04-20-2012 at 06:13 PM.

  8. #8
    Join Date
    Nov 2010
    Location
    Middle of Nowhere, Outer Skin of Space Ship Earth, 1 A.U. from Sol, Outskirts of Milky Way.
    Posts
    2,087
    A fuse near the battery is all you need.
    There is NO need for fuses at both ends.

    The purpose of the fuse or breaker is to keep the wire from melting if there is a short. How? Disconnect the power.

    If the fuse is at the battery end of the wire, then when there is a short the fuse blows and the *whole wire* is now without power.

    If the fuse is at the far end away from the battery and the short is say, somewhere in the middle of the wire (which, it MUST be), then the power will still flow from the battery to the short and the fuse at the far end won't blow because the overload is not flowing through it.

    If you have fuses at both ends and there is a short, then the overload will flow through the fuse at the battery end causing it to blow. Now what is the fuse at the far end supposed to protect? Nothing because the *whole wire* is now without power because the fuse at the battery end shut the whole thing down.


    As for wire size...

    Inverters are a somewhat special case because they pretty much all have a built-in "low-voltage disconnect". So a dip in voltage which most things like lights and radios would ignore, is often enough to cause the inverter to shut down. So - IF you intend to run that inverter at full load - then you have to provide wire large enough to prevent a voltage dip that will put the inverter into shutdown.




    Now, admittedly, I only put in 24,000 hours as a journeyman electrician and field supervisor before I switched over to network engineering...but that's my considered (and educated) opinion.
    ...
    ...
    Current: 76 E-250, bubble-top, self-contained|couple of old Yamaha enduros
    Previous wheelers: 41 Willys|78 FJ40|78 Bronco|84 Bronco|74 Ramcharger|78 Ramcharger|79 D150 PowerWagon|77 D100|79 D400 dually, converted to 4WD, utility bed, 10' Lance|75 Westy|69 Scout, RHD|bunch of others|bunch of bikes|couple of boats|couple of motorhomes|blah blah|so what|not my idea|just doin' what I'm told|wank wank|this space for rent|candy is dandy|but liquor is quicker

  9. #9
    Join Date
    Oct 2011
    Location
    Tucson, AZ
    Posts
    411
    Ok ill just see if i can get some 6 guage, i dont want to be worrying about my truck burning down especially not to safe a quick trip to the store to get more wire lol.
    1994 K2500 Suburban 6.5 turbo diesel, 4l80e, 14bff, g80
    2000 Ford F250, v10, 4x4
    2010 Toyota Carolla S (My DD)
    2013 Ford Fusion (Her DD)
    1992 K2500 Suburban 454tbi, 4l80e, 14bff g80 (Sold but miss it)

  10. #10
    Join Date
    Nov 2010
    Location
    Middle of Nowhere, Outer Skin of Space Ship Earth, 1 A.U. from Sol, Outskirts of Milky Way.
    Posts
    2,087
    Quote Originally Posted by lqdchkn View Post
    According to the table I use (near the bottom) http://www.rbeelectronics.com/wtable.htm
    The table at the bottom of that page is a fire waiting to happen. That table says that it's okay to run 200 amps though a 10 gauge wire if the wire is 3 feet long.


    According to the U.S. National Electrical Code, #10 copper is allowed to carry up to 55 amps, IF the wire insulation is rated to 90 degrees centigrade. 50a with 70 degree rated insulation and 40a with 60 degree rated. And even then - those ratings are only for conductors in "free air" (not enclosed).

    It's covered in Section 310:

    http://www.houwire.com/products/tech...rticle310.html

    The specific section we're looking for is 310.17:

    http://www.houwire.com/products/tech...cle310_17.html

    But even that only covers up to an ambient temperature of 30C (86F). For hotter ambient temps you have to use a different table.



    That's for "power transmission". There is another table which allows #10 to carry a few more amps (but NOT 160 more!) if it's used as "chassis wiring". Chassis wiring is "short lengths inside of a machine". I.e., inside of a Mr. Coffee, welder, radio, inverter, etc.

    Automotive wiring is NOT "chassis wiring" it's "power transmission".



    But of course...the NEC doesn't really care about anything below 50v. Down there, you're on your own and can get away with just about anything. And why not? Auto, truck and RV manufacturers do all sorts of nutty stuff; why not us?


    200 amps through a #10? You can. I won't.
    ...
    ...
    Current: 76 E-250, bubble-top, self-contained|couple of old Yamaha enduros
    Previous wheelers: 41 Willys|78 FJ40|78 Bronco|84 Bronco|74 Ramcharger|78 Ramcharger|79 D150 PowerWagon|77 D100|79 D400 dually, converted to 4WD, utility bed, 10' Lance|75 Westy|69 Scout, RHD|bunch of others|bunch of bikes|couple of boats|couple of motorhomes|blah blah|so what|not my idea|just doin' what I'm told|wank wank|this space for rent|candy is dandy|but liquor is quicker

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •